How to switch 3 resistive consumers (heaters), each having a current consumption of nearly 16 A alternate & ELECTRICALLY SAFELY (German standards)?
So that only one of them heats at a time and the 16 A of the supply line will not exceed.
Suggestion No. 1 (parallel with circuit breaker):
3 electrical contactors (25 A) connected in parallel, are switched on and off by a microprocessor using a relay. The program (which will not be discussed in detail here) ensures that only one contactor activates a consumer and switches the others off.
Problem: A bug or a crash could result in the circuit not working properly and thus possibly switching on 2 or 3 contactors, increasing the load to 32 A or even 36 A.
In this case, in order to have an electrically safe system, is it sufficient to put a 16 A circuit breaker in the supply line of the contactors to ensure a separation? What cross-section should the wiring have for this?
Suggestion No. 2 (changeover switch in stages): 1 changeover contactor, switches between consumer 1 and another 25 A changeover contactor. Consumer 2 is connected to this and another 25 A changeover contactor. Consumer 3 is connected to this. The microprocessor switches the contactors so that either consumer 1, 2, or 3 is active. A big click concert begins.
Advantage: Because they are all changeover contactors, even if there is a bug or the microprocessor/program crashes, it is guaranteed that the current only ever flows to one consumer and can therefore never rise above 16 A.
Is it necessary to design an electrically safe system according to suggestion 2, or is a circuit breaker in the upstream according to suggestion 1 sufficient to make it safe?