I have a project which requires me to interface a 24VDC output module (PLC) with a rather outdated 5V TTL input module.

From the schematics of the old module I can draw the conclusion that it uses +5V as a reference for all the inputs and 0V to activate the input.

I found the following module: MICROOPTOMOS 12-28VDC/5VTTL which I can activate using a 24V signal and it outputs 5V TTL.

The schematic of the module is this:

enter image description here

My question is, how would I go about wiring the module in the way that it "pulls" to the ground the 5V TTL input in order to activate it?

\$\endgroup\$
1
  • \$\begingroup\$ If you want to reverse the output logic you can use any TTL NOT or NAND. \$\endgroup\$
    – user130872
    Commented Mar 17, 2020 at 7:31

1 Answer 1

1
\$\begingroup\$

Judging by the Schmitt trigger symbol in the receiver this module will output a 'high' when the input is on. You want the reverse. You could use an open-collector transistor to do this or you could reverse the output logic in the PLC. Connect up to your +5 V and 0 V and wire OUT to the TTL input.

Alternative solutions:

schematic

simulate this circuit – Schematic created using CircuitLab

Figure 1. Three options.

  • (a) A small relay gives isolation and easy fault-finding. Use one designed for signal-level currents. These work well if frequency of operation is not too high.
  • (b) An opto-isolator has no wearing parts and can handle high frequencies.
  • (c) If isolation is not required a simple open-collector transistor will pull down the TTL input.

enter image description here

Figure 2. Use a DIN rail component carrier to make an industrial standard custom module for your interface circuits.


From the comments:

So by using a reverse PLC logic, when the output of the PLC is low (ergo the device is not "activated" it should pull the input to GND).

Be careful here. You need to ensure that your solution can't put 24 V DC onto a 5 V input. A typical 24 V PLC output will give 24 V or nothing - and nothing means open-circuit, it doesn't mean 0 V. You need a level converter (24 V to 5 V) and then you need to check your logic is the right direction. Since the PLC is active high and TTL is typically active low you may need to invert the logic. If the interface will do that you don't need to do anything else. If the interface won't then have it done in the PLC logic.

\$\endgroup\$
2
  • \$\begingroup\$ Thank you. So by using a reverse PLC logic, when the output of the PLC is low (ergo the device is not "activated" it should pull the input to GND. As for alternative solutions, I am constrained by using already tested commercial sollutions, hence the microoptomos \$\endgroup\$
    – Stefan
    Commented Mar 17, 2020 at 12:15
  • \$\begingroup\$ See the update. \$\endgroup\$
    – Transistor
    Commented Mar 17, 2020 at 14:12