7
$\begingroup$

Neutral wire has a V same as ground i.e almost 0. Also it carries some current. So if we touch the wire don't we to become a part of the circuit? Even if we are on the ground and current should flow through us, but I read we don't get a shock as there is no potential difference between ground and neutral wire, but the current was already flowing from live wire (220 V) to 0, so shouldn't we get a shock?

$\endgroup$
18
  • 13
    $\begingroup$ Current only flows when there is a potential difference. $\endgroup$ Commented Nov 16, 2020 at 19:28
  • 1
    $\begingroup$ The question contains the term “potential difference”. It’s good that you are aware of this term. The key word for this comment is “difference”. The difference between the live and neutral/ground wires is 220 V (or whatever it is for your electricity network), and that is all that matters. Usually we just define the neutral/ground wires to have a potential of exactly zero (assuming neutral and ground are at the same potential); then the live wire’s potential equals the potential difference between live and neutral/ground. $\endgroup$ Commented Nov 17, 2020 at 8:55
  • 1
    $\begingroup$ If you touch the neutral wire in a live circuit, whether it be a lamp, an appliance or something else, it is the same as touching the active wire. It is only "safe" to touch the neutral wire when there is no current flowing, just as it is "safe" to touch the earth wire (when one exists). That is, "safe" is relative. $\endgroup$
    – Mick
    Commented Nov 17, 2020 at 9:21
  • 2
    $\begingroup$ I have had a shock from a neutral wire! $\endgroup$
    – Rodney
    Commented Nov 17, 2020 at 10:42
  • 3
    $\begingroup$ @AryanBeezadhur nope, I was there, it was not static. It was caused by some "work in progress" wiring. As several people have pointed out it is easy for the neutral to become hot due to a fault condition. Line and neutral reversed by installation error is also more common than you might think. And I have seen plenty of inverters which actually have a split phase output, so the neutral isn't 0V relative to earth, and it will light up a neon screwdriver. $\endgroup$
    – Rodney
    Commented Nov 18, 2020 at 13:48

4 Answers 4

44
$\begingroup$

Do not touch even the neutral wire in a live circuit! There are numerous failure modes that could make you dead wrong about not getting shocked.

The neutral wire does have current going through it. However, we do not get shocked when we touch something with current going through it, we get shocked when current goes through us. In this case all of the current that enters one end of the section of wire we are touching also leaves the other end. None goes through us so we don’t get shocked.

Why does no current go through us? From the perspective of a circuit we are, to a first approximation, just a big human shaped resistor. The current through a resistor is proportional to the voltage across it. Since the neutral is at the same voltage as the ground, both our head and our feet are at 0 V. So the voltage across us is 0 V and therefore the current is 0 A.

$\endgroup$
13
  • 11
    $\begingroup$ Mandatory ElectroBOOM link: youtube.com/watch?v=XDf2nhfxVzg $\endgroup$
    – Andrew
    Commented Nov 16, 2020 at 22:46
  • 7
    $\begingroup$ You should never touch plugged in wires or outlets period without testing. Always test regardless of what you think is "turned off". Outlets are more than capable of killing you (it can kill about 100 of you in parallel if setup right). $\endgroup$
    – Nelson
    Commented Nov 17, 2020 at 7:15
  • 1
    $\begingroup$ I feel this is missing something. Say you touch the neutral wire half way along then the current at that point has not yet reached ground and will continue flowing. So why does it choose to flow through the wire and not the person touching the wire? This feels like what the question is asking and doesn't seem to have been covered here explicitly. I assume its because the bug human shaped resistor has a massively higher resistance than the remaining part of the wire and that there is in fact a very very small potential difference, but these two factors just mean that the current is undetectable $\endgroup$
    – Chris
    Commented Nov 17, 2020 at 11:20
  • 3
    $\begingroup$ @Dale: I'm not sure it is but maybe I just explained myself wrong (or am making some bad assumption somewhere). If I am reading you correctly you are saying that the point on the neutral wire I am touching is at zero. That my feet are at zero and that ground is zero. By extension of that logic it feels like I can conclude that the current also doesn't flow in the wire from the point I am touching the wire to its neutral terminal since the potential difference there is zero too. This is clearly wrong though because we know the current is flowing in the wire. $\endgroup$
    – Chris
    Commented Nov 17, 2020 at 12:42
  • 2
    $\begingroup$ @Chris to a first approximation the wire is an ideal conductor. It does not require a voltage difference to carry a current. Do not universally associate current with voltage difference. It is only true in the specific case of a resistor which is why it is important to state that the human behaves as a resistor $\endgroup$
    – Dale
    Commented Nov 17, 2020 at 12:55
22
$\begingroup$

Why don't we? Actually we could!

Your first line is the assumption which will kill you. Literally.

Neutral wire has a V same as ground i.e almost 0.

In a perfect world, with perfect zero-impedance electrical conductors everywhere, there is no voltage between neutral and ground. In that perfect world, you could safely touch the neutral wire.

Surprise - we don't live in a perfect world...

Electricity transmission doesn't actually have a neutral. Instead it has 3 wires which all have AC on them, where the AC waves on each are out of step with the others. When the electricity gets to your local substation near your house, it goes through a transformer to step down the voltage, and also to kind of "add" the three AC signals. Because the AC voltage waves are out of step with each other, adding them together like this gives a "zero" voltage in the middle, which is the neutral.

To keep the neutral close to ground, it's wired to ground (a physical metal rod into the earth!) through some resistance. It can't be tied to ground too well though, because lightning strikes nearby would go back up the neutral and be incredibly dangerous. (They still can, by the way, but the damage is mostly fairly low because of this.)

Separately, your house also has a physical metal rod into the earth which is connected to the ground points of all your outlets.

So how can this go wrong...?

Well, "ground" here isn't "ground" elsewhere. That's why your house has its own metal rod into the earth. Various things (lightning, chemical reactions in the soil, friction of air over the ground, air humidity, just for examples) make for voltage differences between places. Famously, that's why cows can be killed by a nearby lightning strike - there is enough voltage between each foot, across the ground they're standing on, to electrocute them. So even if the neutral was at "ground" at the transformer, it might not be by the time it reaches your house.

Or connections can get broken. If your house earth becomes corroded or breaks, or the same thing happens at the transformer, all bets are off on whether you're at ground or not.

Or you can get a short-circuit from live to neutral. In theory this should trip a breaker. But suppose you don't have a breaker, or someone has replaced a fuse with a nail in an old house. The resistances along live and back along neutral will be roughly equal, so the neutral wire at your outlet will be around half the live voltage. (And then the wire insulation tends to burn and set the house on fire, but that's a separate problem.)

Or you can get a fault in electricity transmission where one phase connection is broken. Instead of the three phases adding together to cancel out and produce the neutral, now you've got a damn great AC voltage on the neutral. Usually there is protection against this getting out, so all power should be shut off if this happens, but in a rural setting with older kit (or on somewhere like a farm where it's managed by the farmer) I would not bet my life on it.

Or more ironically, something somewhere else might have a fault where it's shorted live to earth. You might be safe to touch neutral (apart from the issues above), but if you held onto earth in one hand and neutral in the other, it'd be the earth which kills you.

Just a few examples there. I'm not pretending this is an exhaustive list of the ways you can kill yourself with the neutral - I'm just trying to give you a flavour of why this is a bad idea, and why your incorrect assumption proves fatal to so many people every year. Don't add to those statistics.

$\endgroup$
2
  • $\begingroup$ Well.. at least here there was the concept of 'classical grounding' so the outlets were supplied by two wires and in the outlet neutral was connected to ground to provide ground. Usually metal housings of devices are connected to the ground pin, so a lot of people were touchen the neutral wire when touching any electrical appliance with a metal casing. Havent heard of people getting shocked (but maybe havent heard enough). But I agree: dont do it intentionally $\endgroup$
    – lalala
    Commented Nov 17, 2020 at 17:22
  • 1
    $\begingroup$ @lalala They most certainly have been shocked, and people have died. That's why new standards require double insulation instead of simply grounding the chassis. If everything is setup correctly, then it is safe, but if something isn't wired correctly, then it is possible for the neutral (and even ground!) to carry current and hurt/kill someone. $\endgroup$
    – Nelson
    Commented Nov 18, 2020 at 4:06
8
$\begingroup$

if we touch the wire don't we to become a part of the circuit?

"Circuit" comes from the same Latin word as "circle," or "circus." A circuit is a loop. The only way you can ever have a steady flow of electric current is if it flows around a loop. If you touch a wire, but you are insulated from everything else, then you aren't part of any loop, and there can be no steady flow through your body. But...


...It gets a little more complicated when we're talking about Alternating Current (AC), because then we can talk about current "flowing through" a capacitor even despite the fact that the two terminals of the capacitor are electrically insulated from each other.

Any time some electrically conductive thing comes near some other electrically conductive thing, there is weak capacitance between them. Notably, there always is weak capacitance between yourself and Earth.

Even if you are well insulated from everything else, you still will feel a strong "tingle" if you touch the "hot" wire in a circuit because a tiny amount of AC current is able to flow in a loop from the generating station, through the hot wire, through your body, through the capacitance between your body and Earth, and through the Earth back to the Earth wire at the generating station.

You aren't supposed to feel any tingle* if you touch the neutral wire, because the neutral wire should be connected to Earth someplace not too far from where you are standing. Effectively, both ends of the "capacitor" are connected to the same thing (Earth), and so it's not really part of any loop or circuit.


* But note what other answers already have told you. What is supposed to be is not always the same as what actually is. Touching the neutral still is risky because a fault in the wiring could cause a supposed-to-be-neutral wire to actually be "hot."

Don't go around touching live circuits.

$\endgroup$
6
$\begingroup$

Neutral is near to 0 v, lets say 15v in a domestic installation. As all wires has some low resistance (lets say 5 ohm as example), we can model this system as a point of low voltage (15v) with a low resistor (5 ohm) connected from it to real ground (0v).

When someone (don't do that at home) touches the neutral wire, the change in the circuit is that appears a new connection path from the touch point, across the body, to the ground. The body has an (usual) impedance bigger to 1000 ohm (it depends of person, fingers pressure, conditions, shoes, ...).

Now, the circuit is a parallel of connection of two "resistors" from neutral touch point to ground: the wire (5 ohms) and the body (1000 ohms). By circuits law, the amount of current that will go across the body will be 5/(1000+5)=0.5% of the total current. Usually, that means a level of current that can not cause big injuries.

However, these values are too near to dangerous current intensities and, in some scenarios, a really dangerous current can go across the body.

Don't do that at home.

(a comment about biology: if you must touch a wire -don't do it-, touch it with the reverse of the fingers. In case of shock, muscles tends to close the fingers, so, the fingers will jump out of the cable contact. Instead, if you touch with the internal side of the fingers, you risk that shock closes the fingers around the cable, making it a deadly and insurmountable closure).

$\endgroup$

Not the answer you're looking for? Browse other questions tagged or ask your own question.