The figure shows a toy model for power transmission using ideal transfomers.
In this model, the phase angle between the voltage across the load and the current is zero.
Let's take the load voltage as the reference, i.e., \$ \tilde{V}_{L}=30V \angle 0°\$. The load is resistive, so the current is in phase with the load, i.e., \$ \tilde{I}_{L}=1A\angle 0°\$.
Therefore, the current in the transmission wires is going to be \$ \tilde{I}_{T}=0.5A\angle0°\$ and the voltage across the primary of the second step down transformer is \$\tilde{V}_{p2}=100V\angle0°\$.
Applying KVL in the loop between the two transformers, one concludes that \$\tilde{V}_{s1} =100V\angle0°+0.5A(20\Omega)\angle0°=110V\angle0°\$.
Therefore, \$\tilde{V}_{p1}=220V\angle0°\$ and \$\tilde{I}_{G}=0.25A\angle0°\$
How could this be the case? Assuming everything is ideal, shouldn't the magnetizing current, \$\tilde{I}_{G}\$ in this case, lag the voltage \$\tilde{V}_{p1}\$ by a \$\frac{\pi}{2}\$ angle?
Reference of the figure:
I made it myself