I'm measuring the 0-10V pressure output of a pressure sensor with a LOGO! smart relay (PLC). I would like to make sure that the pressure sensor is working even when I'm measuring nearly zero values with the device. My idea was to connect the other output (4-20mA) of the sensor to the LOGO!'s digital input to make sure that the sensor is working. I would do this beacause the LOGO! only has voltage analog inputs so I can't use the 4-20mA directly in the analog input. The input resistance of the digital input is 80k and the 4-20mA output of the sensor provides nearly 24V (which is the supply voltage) when such a high impedance is present between the output pin and the common ground. So my purpose would be to make sure if the pressure sensor has supply voltage therfore it is probably working. (Unfortunately when a nearly zero pressure is measured the 0-10V output gives 10mV which is a very small value to decide if the pressure sensor is working at all.)
I've tried and it was working. The current was only 0.33mA coming from the 4-20mA output and flowing into the digital input. The voltage dropped at the output by 0.2V. Eventually I measured a logical high value at the digital input so it was working, but I have concerns that in the long term this usage may demage the sensor's output. I dont't have the particular circuit diagram of the pressure sensor's current output but as I understood there aren't major differences between the implementations. Here is an exaple I found: https://www.analog.com/en/design-center/reference-designs/circuits-from-the-lab/CN0314.html#rd-overview
Does someone know if this soulution could work in the long run?