We are planning to install a switchboard in one of our garages. The MCCB (moulded case circuit breaker) is used as a main incomer which has silver plated copper terminals. The aluminium busbars are used as a conductors. While reading the IEC 60943 standard, however, I came across the anodic index of aluminium when used with respect to silver. As per the standard, the galvanic cell creates a potential difference of 770 mV which is greater than the threshold of 350 mV.
While several industrial panels and switchgear recommend to use silver plated aluminium, some do not recommend it. The current scenario uses a 630 A MCCB where the elevated temperature levels may reach 105 C. I have even read that galvanic corrosion is aggravated when the temperature reaches elevated level.
Is it really okay to connect the aluminium busbar to the MCCB (silver plated copper) terminals?
If yes, is there any concrete standard to prove this, or is there any standard that recommends to conduct a test to evaluate the joints susceptible to galvanic corrosion?
I have read this question, but it doesn't answer my question.
Also almost all the manufacturers recommend to use tin plating, but tin with silver leads to potential difference of 470 mV which is greater than the 350 mV threshold value as per the aforementioned standard. Please note that we use contact aid compound such as petroleum jelly which to some extent halts the corrosion.
Please note that this question is been migrated from the home improvement site.
Adding an image of reference to IEC 61439-2 regarding operating humidity conditions: