4
\$\begingroup\$

I was looking at these overhead power lines and wondering what the insulators and bypass cables (circled in red) are for? Overhead power lines

Are those five small discs in each segment ceramic insulators? Are the bypass cables conductors?

On closer inspection it looks like they might be some sort of splice or tensioning device, which maybe isn't rated for current. But then, the bypass connectors on the right side of the splice don't exactly look like proper power conductors either....

\$\endgroup\$
3
  • 1
    \$\begingroup\$ I'm betting the cables broke there (and were patched), or three new cable lengths were attached there (when it was built.) But this is only speculation. \$\endgroup\$
    – rdtsc
    Commented Aug 4, 2021 at 20:11
  • 1
    \$\begingroup\$ My guess is that they're a form of low-cost emergency disconnect. Someone could reach up with an insulated hook and pull the bypass wires loose from the right-hand connector thingies. But to reconnect, someone would have to go out with a bucket truck. Usually, such disconnects are located closer to a pole, and sometimes have a handle so that they can be operated from the ground, but that would be more expensive. \$\endgroup\$
    – Dave Tweed
    Commented Aug 5, 2021 at 0:51
  • \$\begingroup\$ If you look closely, the connections to the right of the insulators are the same as the connections by the pole going down to fuses. Those connections are designed to be installed or removed using "hot sticks" - long insulated poles - so the power company techs don't have to get near the live high voltage wires. \$\endgroup\$ Commented Aug 5, 2021 at 2:23

4 Answers 4

2
\$\begingroup\$

According to a lineman friend of mine, that is a “flying 8”. He said they use them when doing restoration work. That way they can open the circuit easily in locations where they don’t already have a switch. I’m sure the lingo varies from place to place.

He also told me that they usually go back and take those down unless it is a trouble line where they might just leave it there (preferably would have a switch instead to make it easier to operate as @DaveTweed mentions in his comment.

\$\endgroup\$
2
\$\begingroup\$

I found a lineman who works in the city where the photo was taken and he explained the following: That's a splice that is typically done when hanging the lines when one reel of cable runs out and they have to connect it to the next one. (He also said that his union would normally cut the cable so the splice is done at the nearest pole, but in this region they contract out these installations and the contractors have "different" practices.)

The insulators are there because the splice has steel components that aren't rated for conduction. So they install the aluminum jumpers shown.

HV splice with jumpers and stirrup circled

The square piece they connect to on the right (circled above in yellow) is a copper bracket called a "stirrup." If it's ever necessary to disconnect at the splice they can use a hot stick (they call it a "shotgun") with a hook that grabs the eyebolt and can unscrew it to release the jumper cable.

\$\endgroup\$
2
\$\begingroup\$

On top of what is discussed here, I asked one of my friends, and he said it is also used for controlled cable tension. It provides the same cable tension, but it's weaker than the continuous cables. It provides a safe break point if something bad happens and one of the poles falls down. If there are no weak points, it could drag the rest of the poles down. Pole fall down (Image source) But having such a connection with controlled tension provides a safe point in such events. If poles start to fall, instead of dragging the rest of the poles, the cable will separate when it reaches this connection, and the rest of the cables are safe. The next poles to this connection also usually have some cables that are used to fasten the pole to the ground to be able to compensate for the tension along the cable (weight of the cable) from the other side of the pole if this connection breaks.

\$\endgroup\$
-1
\$\begingroup\$

These are unitaries (poly insulators) used for limiting outage impact to customers. If a line cannot be isolated with a switch or tap these can be cut in to restore up to this point or to isolate a piece of equipment or line.

\$\endgroup\$
2
  • 3
    \$\begingroup\$ Since there are already two answers consistent with each other and upvoted, do you have a trustworthy source for your claim? \$\endgroup\$
    – MiNiMe
    Commented Oct 16, 2023 at 1:31
  • 1
    \$\begingroup\$ I can't even see how this is saying something different from the other two answers. \$\endgroup\$
    – feetwet
    Commented Oct 16, 2023 at 2:15

Not the answer you're looking for? Browse other questions tagged or ask your own question.