Advice and idea's please
The location of the subpanel has been moved from the side of the house to now the front. Coming out of the attic we would have to be in the Eave straight down. There is not enough space to accommodate a 2" PVC 90 going down. There is no room to access a condulet fitting cover thought about using that.
Can I set a 12 by 12 J box in attic and come out of that with liquid tight metallic raceway to the subpanel I will more than likely have to install a little unistrut depending on where we come out. Can't come out flush due to the closeness of the eave meeting the side of the house.
Everywhere that I have looked and read and searched and even the WAC says Outdoor wiring (120/240 volts) exposed to moisture and mechanical damage must be protected by rigid metal conduit, electrical metallic tubing, liquid-tight flexible metal conduit, or nonmetallic conduit. The conductors shall be type RW, TW, or equivalent.
I have only found that reference is my thinking correct? The sub is 100 amp the breaker back at the main panel will be a 90 amp