12 votes
2 answers
2k views

Does NEC allow a metal box to carry the ground connection between separate conductors?

I found this box: You can see that most of the conductors have their grounds crimped together in the deep part of the box. A box extension was added to this at some point, so it is rather deep, but ...
Ryan Mortensen's user avatar
7 votes
3 answers
1k views

Best, and acceptable, connector for 12 to 20 ground wires in a junction box?

In a junction box with about 12, and may grow to 20, cables of size #14, #12, #10 what is the best, and alternative connectors to join all the ground wires together? Can I install a ground block, the ...
jay613's user avatar
  • 41.8k
0 votes
1 answer
93 views

Proper grounding of old fuse panel now turned J-Box

I am working on my old house from the early 1900s. It has 100A service, a 6x15A FUSE panel that was turned into a sub panel powered by 2x 20A circuits from a small "newer" 100A breaker panel....
Dentpusher's user avatar
2 votes
2 answers
2k views

What's the proper way to extend wiring into a replacement panelboard?

I'm planning a replacement of a 1960s-vintage subpanel in my home's garage/garage apartment. Power feed from the service entrance is through EMT, which I'll have to use as the grounding means as it's ...
ehbowen's user avatar
  • 439
0 votes
1 answer
723 views

Mounting lug to junction box

I need to bond 10 ga stranded EGC to a metal junction box. I’d like to use something like this lug. The box will be screwed to a floor joist in the crawl space under my house. Does this lug need to be ...
Rick's user avatar
  • 545
3 votes
3 answers
2k views

Is my non-standard outlet box grounding screw code-compliant? (US in 2022)

I'm installing GFCI outlets in my 1950s era existing kitchen counter wall boxes. The metal boxes in the wall have a number of holes in them that I thought were for standard green grounding screws, but ...
Armand's user avatar
  • 4,448
2 votes
3 answers
10k views

How to properly bond metal junction box with 6 AWG conductors

What is the appropriate way to bond a metal junction box containing a receptacle wired with 6 AWG wire? It seems that most metal junction boxes have a 10-32 tapped hole to accept a ground screw but ...
John Hodge's user avatar